Connecting my Sawstop to power (2 pole 230 from 3 pole 230?)
Forum topic by mctabish posted 05-01-2015 02:40 PM 1143 views 0 times favorited 9 replies Add to Favorites Watch
View mctabish's profile
mctabish
3 posts in 1025 days
05-01-2015 02:40 PM
I just got my Sawstop, 5hp single phase and tried to connect it to the power (hardwired)
My wall has 4 wires (black, white, red and green)-also single phase
My sawstop has Black white and green. The manual says if I am using 4 wire, to disregard the red.(This saw does not use a neutral line. SawStop recommends the use of a 3-wire cable or conduit, with the black and white wires connected to power and the green wire connected to a grounded metal permanent wiring system or equipment ground.
If a 4-wire cable or conduit with a neutral wire is used, the neutral line should be capped with a wire nut or connected to the unused center terminal)
I did this and the saw starts up very slow and then powers down.
I called Sawstop,it seems like it is only getting 110v. but they could not advise me.
How would I hook this up?
Thanks, Bruce
9 replies so far
View AZWoody's profile
AZWoody
1258 posts in 1127 days
#1 posted 05-01-2015 02:51 PM
Usually the white is the neutral. From the wall.
The black and the reds are your hot wires for running the 220. They should be what’s running to the saw.
So I would think you would run the black and red from the wall, to the black and white of the saw.
View bonesbr549's profile
bonesbr549
1490 posts in 2970 days
#2 posted 05-01-2015 02:53 PM
Ok this is easy. You are getting only 110v. We are also assuming you have that 4 wire coming from the box correctly. Basically you need two hots and a ground for your saw. Take a multimeter which every shop needs. Read the voltages to neutral to find your two hots. (you can also look in your panel and see which wires have the hot.
Normally Green is ground, White is neutral, black is hot, and other color can be hot as well.
I’ll put a link to an image. Again this is what you should see. I always and I mean always, put a meter on my lines to find each hot. Put one meter lead on neutral and the other on the black and you should see 120v. Do the red, and neutral, and probably you will see 110v. Then put one lead on the black and then the red, and you will see probably 235-240v. Once you know your hots, then wire to your saw, and the ground. It will be solved.
I had a bigger problem and mine would not start at all. I was mad frustrated, then found the lockout switch was off . Oppsie!!!! Flipped it and all was good.
Latter, you will love that ICS! Love mine!
http://farm3.static.flickr.com/2608/4010766507_7445e8afb3_o.jpg
4873 posts in 2396 days
#3 posted 05-01-2015 03:22 PM
With a cheap VOM, you read which wires are hot and go from there. Like bones said, you need 2 hots and a ground.
View crank49's profile
crank49
4029 posts in 2874 days
#4 posted 05-01-2015 04:39 PM
”My sawstop has Black white and green. The manual says if I am using 4 wire, to disregard the red.(This saw does not use a neutral line.”
Can’t imagine where they got that logic. There is no normal relationship of red to neutral.
In a single phase or split single phase 4 wire system, the ground is green, the white is neutral, the red and black are both hot. Each hot wire is normally 120 volts measured to neutral or ground. Measured between two hot wires the voltage should be 240 volts.
By the way, one hot can be 110, 115 or 120 volts and two hot wires can be 220, 230 or 240 volts. Voltages are not precise and change during the day depending on demand load on the utility. They generally try to keep it on the high end of the range.
The system that is contrary to accepted practice here belongs to SawStop. They should have black, red and green wires for you to connect to.
mctabish
#5 posted 05-02-2015 04:40 AM
Thanks! I will try these suggestions tomorrow!
Bruce
View TheFridge's profile
TheFridge
8852 posts in 1389 days
#6 posted 05-02-2015 04:54 AM
Should be black and red.
#7 posted 05-03-2015 11:30 AM
Bruce, did you get it hooked up?
mctabish
#8 posted 05-03-2015 11:58 AM
I sure did! and this baby just purrs! Sweeet!
Now to get it all tweaked out and make my cross cut sled!
Thanks all!
Bruce
bonesbr549
#9 posted 05-03-2015 12:42 PM
Congrats. How about some pics